Hey Won,
This output looks familiar, I think I have worked on this before with
another FreeIPMI user ...
=====================================================
Reserve SEL Request
=====================================================
[ 42h] = cmd[ 8b]
=====================================================
Reserve SEL Response
=====================================================
[ 42h] = cmd[ 8b]
[ C1h] = comp_code[ 8b]
ipmi_cmd_reserve_sel: bad completion code: command invalid/not supported
So this is a bug on HP's part, but shouldn't really be a problem b/c I
have code to work around it (you can tell b/c there is more
output :-) ...
=====================================================
Get SEL Entry Request
=====================================================
[ 43h] = cmd[ 8b]
[ 0h] = reservation_id[16b]
[ 0h] = record_id[16b]
[ 0h] = offset_into_record[ 8b]
[ FFh] = bytes_to_read[ 8b]
=====================================================
Get SEL Entry Response
=====================================================
[ 43h] = cmd[ 8b]
[ CBh] = comp_code[ 8b]
CBh = sensor not present
Something seems amiss in the HP IPMI. Do you have any HP software that
works? Maybe it only works for HP software and none of the open source
software out there.
Al
On Fri, 2009-04-03 at 18:21 -0700, Won De Erick wrote:
> Hi All,
>
> sending the debug output.
>
> Thanks,
>
> Won
>
> --- On Fri, 4/3/09, Al Chu <address@hidden> wrote:
> > Hey Won,
> >
> > > One thing left is how i can into the SEL. I tried this
> > with other tools. None of them gave an output. :(
> >
> > Do you mean you can't access the SEL in multiple IPMI
> > software?
> >
> > Can you send me the --debug output from running
> > ipmi-sel? Let's see what the problem is.
> >
> > Al
> >
> > On Fri, 2009-04-03 at 11:57 -0700, Won De Erick wrote:
> > > --- On Fri, 4/3/09, Al Chu <address@hidden>
> > wrote:
> > > > Hey Won,
> > > >
> > > > The reason for what you're seeing is described in
> > the
> > > > ipmimonitoring
> > > > manpage.
> > > >
> > > > ---
> > > > Interpretation rules have not been written for
> > all sensors
> > > > permutations
> > > > and types. Users may notice some sensors output
> > in
> > > > ipmi-sensors(8) do
> > > > not output in ipmimonitoring. If sensor
> > interpretation
> > > > rules are needed,
> > > > please contact the FreeIPMI maintainers.
> > > > ---
> > > >
> > > > Looking at your sensors output below, there are
> > three OEM
> > > > sensors that I
> > > > can't interpret b/c I don't know the
> > interpretation rules
> > > > for them. The
> > > > Power Unit Device Install and Fan transition
> > > > interpretations were
> > > > recently added in 0.7.3. So if you update
> > to atleast
> > > > 0.7.3, those
> > > > readings should show up in ipmimonitoring.
> > > >
> > > > As for why Temperature Sensors aren't showing up,
> > this
> > > > corner case for
> > > > HP machines also appears to have been fixed in
> > 0.7..3.
> > >
> > > Thank you for the tip. I installed the latest, 0.7.6,
> > instead.
> > >
> > > hpdl380-fbsd71r# ipmi-sensors
> > > 1: UID Light (OEM Reserved): [OEM State = 0000h]
> > > 2: Int. Health LED (OEM Reserved): [OEM State =
> > 0000h]
> > > 3: Ext. Health LED (OEM Reserved): [OEM State =
> > 0000h]
> > > 4: Power Supply 1 (Power Supply): [Presence detected]
> > > 5: Power Supply 2 (Power Supply): [NA]
> > > 6: Power Supplies (Power Supply):
> > [Non-redundant:Sufficient Resources from Redun
> >
> > dant]
> > > 8: VRM 1 (Power Unit): [Device Inserted/Device
> > Present]
> > > 9: VRM 2 (Power Unit): [Device Inserted/Device
> > Present]
> > > 10: Fan 1 (Fan): [transition to Running]
> > > 11: Fan 2 (Fan): [transition to Running]
> > > 12: Fan 3 (Fan): [transition to Running]
> > > 13: Fan 4 (Fan): [transition to Running]
> > > 14: Fan 5 (Fan): [transition to Running]
> > > 15: Fan 6 (Fan): [transition to Running]
> > > 16: Fans (Fan): [Fully Redundant]
> > > 18: Temp 1 (Temperature): 35.00 C (NA/70.00): [OK]
> > > 19: Temp 2 (Temperature): 17.00 C (NA/39.00): [OK]
> > > 20: Temp 3 (Temperature): 30.00 C (NA/127.00): [OK]
> > > 21: Temp 4 (Temperature): 30.00 C (NA/127.00): [OK]
> > > 22: Temp 5 (Temperature): 46.00 C (NA/77.00): [OK]
> > > 23: Temp 6 (Temperature): 30.00 C (NA/127.00): [OK]
> > > 24: Temp 7 (Temperature): 30.00 C (NA/127.00): [OK]
> > > 25: Power Meter (Current): [Device Enabled]
> > >
> > >
> > > hpdl380-fbsd71r# ipmimonitoring
> > > Record_ID | Sensor Name | Sensor Group | Monitoring
> > Status| Sensor Units | Sensor Reading
> > > 4 | Power Supply 1 | Power Supply | Nominal | N/A |
> > 'Presence detected'
> > > 6 | Power Supplies | Power Supply | Critical | N/A |
> > 'Non-redundant:Sufficient Resources from Redu
> > ndant'
> > > 8 | VRM 1 | Power Unit | Nominal | N/A | 'Device
> > Inserted/Device Present'
> > > 9 | VRM 2 | Power Unit | Nominal | N/A | 'Device
> > Inserted/Device Present'
> > > 10 | Fan 1 | Fan | Nominal | N/A | 'transition to
> > Running'
> > > 11 | Fan 2 | Fan | Nominal | N/A | 'transition to
> > Running'
> > > 12 | Fan 3 | Fan | Nominal | N/A | 'transition to
> > Running'
> > > 13 | Fan 4 | Fan | Nominal | N/A | 'transition to
> > Running'
> > > 14 | Fan 5 | Fan | Nominal | N/A | 'transition to
> > Running'
> > > 15 | Fan 6 | Fan | Nominal | N/A | 'transition to
> > Running'
> > > 16 | Fans | Fan | Nominal | N/A | 'Fully Redundant'
> > > 18 | Temp 1 | Temperature | Nominal | C | 35.000000
> > > 19 | Temp 2 | Temperature | Nominal | C | 17.000000
> > > 20 | Temp 3 | Temperature | Nominal | C | 30.000000
> > > 21 | Temp 4 | Temperature | Nominal | C | 30.000000
> > > 22 | Temp 5 | Temperature | Nominal | C | 46.000000
> > > 23 | Temp 6 | Temperature | Nominal | C | 30.000000
> > > 24 | Temp 7 | Temperature | Nominal | C | 30.000000
> > > hpdl380-fbsd71r#
> > >
> > > One thing left is how i can into the SEL. I tried this
> > with other tools. None of them gave an output. :(
> > >
> > > The box is IPMI v2.0-compliant. I can see a lot of
> > logs using iLO.
> > >
> > > Thanks,
> > >
> > > Won
> > >
> > >
> > >
> > >
> > >
> > >
> > --
> > Albert Chu
> > address@hidden
> > Computer Scientist
> > High Performance Systems Division
> > Lawrence Livermore National Laboratory
> >
> >
>
>
>
--
Albert Chu
address@hidden
Computer Scientist
High Performance Systems Division
Lawrence Livermore National Laboratory